I am a data center technician for a financial company in St. Louis, MO. I have my EIT certification and along with my other duties am involved in various projects throughout the company's St. Louis campuses. I was recently asked to perform some basic harmonic analysis at one of the large office buildings characterized by large lighting loads, personal desktop computers, and VFD controlled mechanical equipment. The initial cause for the study was a pitch from a salesman to buy a 3rd harmonic current filter. When a Fluke 43B power quality analyzer was placed on the secondary side neutrals of 3 different transformers in the building some interesting results were obtained.
Case 1:
XFMR2, 500KVA, 480/208,120V , 3 feed cables per phase, 3 neutral cables
RMS readings on one cable per phase were:
A-90.3A @60Hz, 34.9A @180Hz
B-87.7A @60HZ, 44.5A @180HZ
C-52.5A @60Hz, 27.1A @180Hz
Normal neutral readings were
Cable 1- 26.2A @60HZ, 74.4A @180Hz
Cable 2- 31.6A @60Hz, 69.2A @180Hz
Cable 3- 52.0A @60Hz, 90.7A @180Hz
(Accounting for the difference in the neutral cables to that they were taking individually and not simultaneously with loads fluctuating frequently)
An anomaly occurred on the neutral in Cable 1 only. Every 15-20 for a period of roughly 5 seconds a reading with a fundamental frequency of 175 Hz would occur, for example:
Cable 1- 83.5A @175Hz, 8.3A @526Hz
No 60Hz current was shown, the loads are obviously not balanced, as well as this only occurred on 1 cable of the neutral.
Case 2:
XFMR3, 750KVA, 480/208,120V , 5 feed cables per phase, 10 neutral cables
8 of the 10 cables showed a fundamental current of approximately 180Hz, their averages were as folows:
THD-15.5%
Total rms current-21.5 A
Fundamental Frequency-20A @180Hz
3rd Harmonic-3A @540 Hz
DC component- 5-10% of total or about 1-2A
The other two cables were connected to the same neutral bus, but from an addition to the bottom and therefore are of a slightly longer length. Their averages were:
THD-88.7%
Total rms current-17.9A
Fundamental Frequency-8A @60Hz
3rd Harmonic- 16A @180Hz
DC component-negligible
Once again loads are not balanced among the phases. On one cable of each phase these were the readings:
A-50Arms, 50.5%THD
40A @60Hz, 22A @180Hz
B-47.9Arms, 34.9%THD
43A @60Hz, 12.7A @180Hz
C-34.1Arms, 56.2%THD
27A @60Hz
17.5A @180Hz
There was also a third case with XFMR-1, where one of the neutral of five had a similar reading to those with approximately 180 Hz fundamental reading. We have so far been unable to duplicate these readings on other simpler amp meters. I was wondering if any one has come across this situation before, if possibly the Fluke 43B isn’t accurately depicting what’s happening, or has an idea as to what could possibly account for these readings.
There have been many modifications to this building’s electrical distribution from the utility transformers down to the main distribution switchgear since the building was initially built in the 70’s. They have also experienced heating up of the contacts in the utility to generator ATS’s and recently experienced a demolishing fire in one of the ATS’s. Russelectric’s report on the ATS gave possible causes as follows:
“The emergency contacts showed considerable damage due to arcing. Determining when this damage occurred is almost impossible. We know that during the fire the normal utility source circuit breaker tripped. This began the sequence to transfer to emergency power. When the emergency contacts closed, they once again energized the rear compartment subjecting the device to a second high current fault. This is what we call a ‘Close on, Bolted Fault’ an extremely severe operation. These contacts are designed to withstand this type of fault, without welding shut, but arcing damage is inevitable. The ATS had a history of high temperature readings and a flash over on the normal source. The finger clusters were replaced but not the contacts. Proper inspection of the contacts not completed. Contacts were most likely the cause of the high heat and subsequent flash over. …The heat rise as recorded on site was duplicated here in the factory. The main contacts were confirmed as the source of the heating, not the finger clusters as first believed. Both main and Emergency contacts show considerable damage. Damage can be caused by either load transients during transfers or late out of phase closure during closed transition transfers. Damage to main contacts lead to overheating which will have a detrimental effect on finger cluster springs. Springs can loose tension when subjected to heating considerably beyond spec. Loss of tension creates more heat leading to arcing. Eventually the phases will flash over at the point of minimal electrical clearance which is at the finger clusters. The above items were most likely involved in the ultimate failure of [the ATS].”
The reason I included this with the question is to see if anyone else thinks the two could be related and if the strange readings observed were not due to possible unintentional cross-connecting of transformers or neutrals not being connected in a proper manner due to the many changes the building has had at it’s electrical entrance.
Case 1:
XFMR2, 500KVA, 480/208,120V , 3 feed cables per phase, 3 neutral cables
RMS readings on one cable per phase were:
A-90.3A @60Hz, 34.9A @180Hz
B-87.7A @60HZ, 44.5A @180HZ
C-52.5A @60Hz, 27.1A @180Hz
Normal neutral readings were
Cable 1- 26.2A @60HZ, 74.4A @180Hz
Cable 2- 31.6A @60Hz, 69.2A @180Hz
Cable 3- 52.0A @60Hz, 90.7A @180Hz
(Accounting for the difference in the neutral cables to that they were taking individually and not simultaneously with loads fluctuating frequently)
An anomaly occurred on the neutral in Cable 1 only. Every 15-20 for a period of roughly 5 seconds a reading with a fundamental frequency of 175 Hz would occur, for example:
Cable 1- 83.5A @175Hz, 8.3A @526Hz
No 60Hz current was shown, the loads are obviously not balanced, as well as this only occurred on 1 cable of the neutral.
Case 2:
XFMR3, 750KVA, 480/208,120V , 5 feed cables per phase, 10 neutral cables
8 of the 10 cables showed a fundamental current of approximately 180Hz, their averages were as folows:
THD-15.5%
Total rms current-21.5 A
Fundamental Frequency-20A @180Hz
3rd Harmonic-3A @540 Hz
DC component- 5-10% of total or about 1-2A
The other two cables were connected to the same neutral bus, but from an addition to the bottom and therefore are of a slightly longer length. Their averages were:
THD-88.7%
Total rms current-17.9A
Fundamental Frequency-8A @60Hz
3rd Harmonic- 16A @180Hz
DC component-negligible
Once again loads are not balanced among the phases. On one cable of each phase these were the readings:
A-50Arms, 50.5%THD
40A @60Hz, 22A @180Hz
B-47.9Arms, 34.9%THD
43A @60Hz, 12.7A @180Hz
C-34.1Arms, 56.2%THD
27A @60Hz
17.5A @180Hz
There was also a third case with XFMR-1, where one of the neutral of five had a similar reading to those with approximately 180 Hz fundamental reading. We have so far been unable to duplicate these readings on other simpler amp meters. I was wondering if any one has come across this situation before, if possibly the Fluke 43B isn’t accurately depicting what’s happening, or has an idea as to what could possibly account for these readings.
There have been many modifications to this building’s electrical distribution from the utility transformers down to the main distribution switchgear since the building was initially built in the 70’s. They have also experienced heating up of the contacts in the utility to generator ATS’s and recently experienced a demolishing fire in one of the ATS’s. Russelectric’s report on the ATS gave possible causes as follows:
“The emergency contacts showed considerable damage due to arcing. Determining when this damage occurred is almost impossible. We know that during the fire the normal utility source circuit breaker tripped. This began the sequence to transfer to emergency power. When the emergency contacts closed, they once again energized the rear compartment subjecting the device to a second high current fault. This is what we call a ‘Close on, Bolted Fault’ an extremely severe operation. These contacts are designed to withstand this type of fault, without welding shut, but arcing damage is inevitable. The ATS had a history of high temperature readings and a flash over on the normal source. The finger clusters were replaced but not the contacts. Proper inspection of the contacts not completed. Contacts were most likely the cause of the high heat and subsequent flash over. …The heat rise as recorded on site was duplicated here in the factory. The main contacts were confirmed as the source of the heating, not the finger clusters as first believed. Both main and Emergency contacts show considerable damage. Damage can be caused by either load transients during transfers or late out of phase closure during closed transition transfers. Damage to main contacts lead to overheating which will have a detrimental effect on finger cluster springs. Springs can loose tension when subjected to heating considerably beyond spec. Loss of tension creates more heat leading to arcing. Eventually the phases will flash over at the point of minimal electrical clearance which is at the finger clusters. The above items were most likely involved in the ultimate failure of [the ATS].”
The reason I included this with the question is to see if anyone else thinks the two could be related and if the strange readings observed were not due to possible unintentional cross-connecting of transformers or neutrals not being connected in a proper manner due to the many changes the building has had at it’s electrical entrance.