Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

HIGH INDUCED CURRENT FOR CONTINUOUS CROSS BONDING (SOLUTION)

Status
Not open for further replies.

jpbuntales27

Electrical
Nov 3, 2019
2
We have installed 115kV 500sqmm Cable for 6300 meter length and provided 9 JBS all Cross Bond.
When we do the testing and injected 70 amperes we are getting high current from the sheath.
Is there a solution to reduce the sheath current

R Y B
JB1 15.8 21.3 5.5
JB2 5.5 15.7 21.4
JB3 21.4 5.5 15.8
JB4 15.8 21.3 5.5
JB5 5.5 15.8 21.4
JB6 21.4 5.5 15.7
JB7 15.8 21.2 5.5
JB8 5.5 15.9 21.5
JB9 21.4 5.5 15.8

Doc1_kh5rxv.jpg
 
Replies continue below

Recommended for you

Lift the grounds at one end.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
As I read the drawing, you have grounded the sheaths at both ends.
Cross bonding is used to limit the induced voltages.
Current is eliminated by grounding at one end only, usually the feed end.
The sheaths are insulated from ground at the cross bonding points and at the load end.
A separate conductor is used for equipment grounding.
Another option is to let the currents flow and de-rate the cables to allow for the additional heat.
Bill
--------------------
"Why not the best?"
Jimmy Carter
 
What voltages/currents is your test setup applying? What’s the phase angle relationship between the phases?
 