On a incoming service 3phase 240V phase to Phase. 2 legs
are 120 against neutral one leg is 208 V.
The incoming service is 600 A. The high leg has only a 15
HP compressor connected. The air compressor cuts in and out. I am trying to correct the PF which is .85 and .90
on the legs used for lighting etc. and .14 at no load on the
high leg when the compressor runs the PF is .75 [high leg]
the monthly power consumption is 8000 Kwh. Kw demand is 24.
What can be done to improve the power factor on this system.
The voltage THD is 7.5%. The amperage THD is 17%.
Thank you