I recently started at a large chemical company after 20 years at smaller chemical plants as a utility engineer.
Several years ago, this plant retrofitted a boiler with a low NOx burner using only Natural gas as a fuel. During the modification, the manufacturer recommended a boiler shutdown at either 12% and 1.5% O2. They put a 3 minute delay in the shutdown.
We have recently experienced several shutdowns at high O2 with an adverse effect on production. In my 20 years experience with boilers, I have NEVER had a shutdown tied either on high or low O2, only alarms on low. NFPA doesn't require it or O2 analyzers for that matter. I understand there is a reason for the high or low O2 and I am indeed looking into that.
My questions...
Why the shutdown on HIGH O2? Does this have to do anything with a low NOx burner and why?
Does anyone else have boilers without low O2 shutdown? I worked at two other plants that had no O2 shutdown.
I have never experienced any problems running without. If this were a severe problem, I'm sure NFPA would make it a requirement. Sounds like over kill by the manufacturer to me. When you call them, they talk down to you as if they are God's gift to the world of boilers.
Several years ago, this plant retrofitted a boiler with a low NOx burner using only Natural gas as a fuel. During the modification, the manufacturer recommended a boiler shutdown at either 12% and 1.5% O2. They put a 3 minute delay in the shutdown.
We have recently experienced several shutdowns at high O2 with an adverse effect on production. In my 20 years experience with boilers, I have NEVER had a shutdown tied either on high or low O2, only alarms on low. NFPA doesn't require it or O2 analyzers for that matter. I understand there is a reason for the high or low O2 and I am indeed looking into that.
My questions...
Why the shutdown on HIGH O2? Does this have to do anything with a low NOx burner and why?
Does anyone else have boilers without low O2 shutdown? I worked at two other plants that had no O2 shutdown.
I have never experienced any problems running without. If this were a severe problem, I'm sure NFPA would make it a requirement. Sounds like over kill by the manufacturer to me. When you call them, they talk down to you as if they are God's gift to the world of boilers.