chemicalengr
Chemical
- Aug 12, 2008
- 9
A recent centrifugal pump re-build left my client with pump curves (x3) that are "flat" at their lower flow range, to the point that the minimum stable flow is on the flat part of the curve. The pump may be required to periodically operate at the minimum flow, thereby making a high pressure trip for pump protection nearly impossible to implement. API RP 14C recommends that a high pressure trip be present on the pump discharge.
A low flow trip could be implemented as there are flow meters on each individual pump discharge, but there is some concern about the accuracy of the meters.
Each pump is equipped with its own minimum flow control valve and the service is seawater at high pressure (~ 360 bar). The discharge piping is rated for the pump discharge pressure. Therefore, the concern is pump protection as these are large expensive pieces of equipment.
Does anyone have any experience with a similar situation or thoughts on a potential solution?
A low flow trip could be implemented as there are flow meters on each individual pump discharge, but there is some concern about the accuracy of the meters.
Each pump is equipped with its own minimum flow control valve and the service is seawater at high pressure (~ 360 bar). The discharge piping is rated for the pump discharge pressure. Therefore, the concern is pump protection as these are large expensive pieces of equipment.
Does anyone have any experience with a similar situation or thoughts on a potential solution?