I have been asked to evaluate the possibility of using high resistance grounding (HRG) for a new facility. The primary reason is to reduce the possibilities of downtime and equipment damage.
The electrical service is 600V, 800A, supplied by a 500-750kVA utility transformer. The main loads are two 250hp VFD's. One is required to run at all times (though downtime will not be extremely expensive).
Will HRG help reduce potential damage to the VFD's or motors during a ground fault event? The VFD will be protected by fuses and the motor will be protected by the VFD's ground fault protection.
Another advantage to HRG is that a ground fault on the main bus will not cause the main breaker to trip, but is this even a likely occurence? Ground faults downstream should only trip downstream breakers/fuses if everything is coordinated properly. The main breaker is not required to have ground fault protection.
Any opinions would be welcome.
The electrical service is 600V, 800A, supplied by a 500-750kVA utility transformer. The main loads are two 250hp VFD's. One is required to run at all times (though downtime will not be extremely expensive).
Will HRG help reduce potential damage to the VFD's or motors during a ground fault event? The VFD will be protected by fuses and the motor will be protected by the VFD's ground fault protection.
Another advantage to HRG is that a ground fault on the main bus will not cause the main breaker to trip, but is this even a likely occurence? Ground faults downstream should only trip downstream breakers/fuses if everything is coordinated properly. The main breaker is not required to have ground fault protection.
Any opinions would be welcome.