Hello:
I am working on sizing the neutral grounding resistor for a high resistance ( through a distribution transformer) grounded generator. In the first steps, the total system charging current must be determined. I am first gathering the contributions from large cables (500, 750MCM), and wondering if you can please verify that zero sequence capacitance of the cable should be used to determine the charging current. In general, is the zero sequence impedance (of any connected device) the correct to use? Thanks for your help.
I am working on sizing the neutral grounding resistor for a high resistance ( through a distribution transformer) grounded generator. In the first steps, the total system charging current must be determined. I am first gathering the contributions from large cables (500, 750MCM), and wondering if you can please verify that zero sequence capacitance of the cable should be used to determine the charging current. In general, is the zero sequence impedance (of any connected device) the correct to use? Thanks for your help.