HIgh Resistance Grounding: sanity check on choosing cable sequence impedance

Status
Not open for further replies.

brainsalad

Electrical
Apr 16, 2012
33
Hello:

I am working on sizing the neutral grounding resistor for a high resistance ( through a distribution transformer) grounded generator. In the first steps, the total system charging current must be determined. I am first gathering the contributions from large cables (500, 750MCM), and wondering if you can please verify that zero sequence capacitance of the cable should be used to determine the charging current. In general, is the zero sequence impedance (of any connected device) the correct to use? Thanks for your help.
 
Replies continue below

Recommended for you

The resistor would normally be sized based on the maximum fault current and duration rather than the quiescent current.
Regards
Marmite
 
But that maximum fault current must be higher than the charging current, so the question is relevant.

I really don't know, but I suspect that positive sequence charging current is sufficient.
 