Buildtech2
Mechanical
- Mar 6, 2012
- 158
I am currently designing a chilled water plant of total cooling capacity of 2400 tons. There are 4 nos duty water cooled ammonia chillers of capacity 600 tons each. The chillers are water cooled type with evaporative condensers.The total chilled water loop is quite large about 2000 m including both chws and chwr.The pumping configuration is constant primary and variable secondary system.The total chilled water flow is 3600 gpm with 16 degree delta-T. Before performing actual pump head calculations using spread sheet, I always do some rough calculation using thumb rule as follows but I foudn that pump head for the secondary loop is quite high and I have to take a decision if primary / secondary pumping configuration is suitable for this plant or should I consider primary, secondary and tertiary pumping system to minimize the head. Any though on this would be highly appreciated.
Total length of chilled water supply = 1000 m
Total length of chilled water return = 1000 m
Pipe friction loss = 3.5 ft / 100 ft
Total chilled water pipe length = 2000 m = 6560 ft
Total friction loss = 1.5 x system length (ft) x friction rate (ft/100 ft)
Pipe friction rate = 3.5 ft / 100 ft
Total friction loss = 1.5 x 6560 x 3.5 / 100 = 344 ft
Rules of Thumb – BSRIA 2001
0.36 X circuit length =
Pressure in kpa and length in meter.
Total circuit length = 2000 m
Pump head = 0.36 x 2000 = 720 kpa = 241 ft .wg.
Total length of chilled water supply = 1000 m
Total length of chilled water return = 1000 m
Pipe friction loss = 3.5 ft / 100 ft
Total chilled water pipe length = 2000 m = 6560 ft
Total friction loss = 1.5 x system length (ft) x friction rate (ft/100 ft)
Pipe friction rate = 3.5 ft / 100 ft
Total friction loss = 1.5 x 6560 x 3.5 / 100 = 344 ft
Rules of Thumb – BSRIA 2001
0.36 X circuit length =
Pressure in kpa and length in meter.
Total circuit length = 2000 m
Pump head = 0.36 x 2000 = 720 kpa = 241 ft .wg.