jraef
Electrical
- May 29, 2002
- 11,345
Anyone know of a source for high speed Solid State contactors that can switch off an AC motor of around 90A 460V in 11ms? I am using an SCR based contactor now and the disconnect time is approx. 80ms from command, but that is apparently too slow. The client was using an IGBT based contactor for this up until the supplier went under and he is looking for a replacement. Because it did not wait for a zero cross, it cut off power in 7 - 11ms from command (anecdotal, I never saw it work). The application is a 30HP 460V 37FLA high speed cutter motor with a worst case duty cycle of about 6 starts per minute.
The SS contactor is only used as an emergency disconnect when the blades of this machine jam, but I mention the duty cycle because this contactor, upstream from the normal reversing motor controller, will still see all of the starting current from a thermal standpoint. I picked 90A as a rating to derate for the extra current it will see.
So far the 90A SCR contactor is holding up thermally, but they want something faster because they have a 20ms delay on jam detection, plus this disconnect delay, plus the motor field collapse delay of about 28ms before the motor torque is gone and in that time, the high speed blades are at risk for serious damage and or destruction. At the 11ms disconnect with the IGBT contactor they had before, it was apparently fast enough to prevent catastrophic failures. I can't seem to find anyone selling IGBT based contactors for anything other than DC applications.
The SS contactor is only used as an emergency disconnect when the blades of this machine jam, but I mention the duty cycle because this contactor, upstream from the normal reversing motor controller, will still see all of the starting current from a thermal standpoint. I picked 90A as a rating to derate for the extra current it will see.
So far the 90A SCR contactor is holding up thermally, but they want something faster because they have a 20ms delay on jam detection, plus this disconnect delay, plus the motor field collapse delay of about 28ms before the motor torque is gone and in that time, the high speed blades are at risk for serious damage and or destruction. At the 11ms disconnect with the IGBT contactor they had before, it was apparently fast enough to prevent catastrophic failures. I can't seem to find anyone selling IGBT based contactors for anything other than DC applications.