Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

High temperature light fixture florescent lamps

Status
Not open for further replies.

Mohsen1

Electrical
Aug 27, 2002
11


We have light fixture 2X 36 watt, 240 Volt florescent lamps with ballast, and we found MCB always tripped due to damage of the ballast and wiring inside light fixture, then we measured the temperature at light fixture during normal operation we found it reached to 100 C because it is between two furnaces and its required lighting at this area.

Please can you give me name of manufacturer have light fixture with high temperature around 90 C or 100 C with ballast explosion proof Type: Ex s e q d II C T4

 
Replies continue below

Recommended for you

That will be tough... Can you duct make up combustion air or some other air past the fixture? This would probably let the fixture continue to work.
 
Petrel's range might have something suitable. The T4 classification is going to be tough to meet with a IIC gas group.



----------------------------------

One day my ship will come in.
But with my luck, I'll be at the airport!
 
Status