Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

High tension motors 1

Status
Not open for further replies.

kkrishnakumarkk

Electrical
Sep 8, 2012
4
Most of heavy industries and petrochemical High tension motors running in star connection only. I dont know any where hightension motors running through delta connections. If running star only, please give an idea about that
 
Replies continue below

Recommended for you

Makes it possible to have winding differential protection.
 
As David says,
"A delta connection makes it easy to have winding differential protection."
In North America it is common for the star point of star connected motors to be inaccessible and differential protection of a star connected motor generally requires a special order/build motor or a trip to the rewind shop to have the star leads brought out.
In IEC land where motors are commonly arranged for either star or delta connection this may not be an issue. It depends on local codes and practices.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Actually, Bill, I was saying that wye (star) makes differential easier. I'm guessing that by High Tensions, he means medium voltage and an external wye becomes much more common.
 
Yes i meaned it 6.6KV, induction motor, differential ct used in external box of motor. 1500Hp induction motor.
 
Status
Not open for further replies.

Part and Inventory Search