cme
Mechanical
- Jan 16, 2003
- 196
I have been assigned to an air handler replacement project serving a lab of a hospital. The system is 100% OSA, dual-duct and has approx 16,500 cfm at 60 deg supply air to the space. The new system will supply 20,000 cfm and possibly 52-54 deg air range.
At that cfm, the lab will have about 1.5 cfm/SF and the duct velocity will be approx 4000 FPM. This is like a dust collection system. The exist TSP is 7.5" and calcs indicate 3.5-4" ESP for known losses like filters, coils, etc. The new ESP may be 6" using fan laws plus losses due to duct tie-in since this unit is going on the roof.
My question is fitting losses. ASHRAE gives a constant of .12 times the velocity pressure. So that puts me at .12" SP for an elbow since my VP is unity. This doesn't seem close at all.
I have tried Carrier data books and this seems to be all in the same range.
I found a mfr (Aero Dyne) which states their PD is .17" at 2500 FPM. I can use fan laws to est SP drop at 4000 fpm.
Anybody here have any data or experience on rectangular fitting pressure drop for my situation. I'm hesitant on using turning vanes at this velocity not just for SP drop but permanent deformation or blow-out.
At that cfm, the lab will have about 1.5 cfm/SF and the duct velocity will be approx 4000 FPM. This is like a dust collection system. The exist TSP is 7.5" and calcs indicate 3.5-4" ESP for known losses like filters, coils, etc. The new ESP may be 6" using fan laws plus losses due to duct tie-in since this unit is going on the roof.
My question is fitting losses. ASHRAE gives a constant of .12 times the velocity pressure. So that puts me at .12" SP for an elbow since my VP is unity. This doesn't seem close at all.
I have tried Carrier data books and this seems to be all in the same range.
I found a mfr (Aero Dyne) which states their PD is .17" at 2500 FPM. I can use fan laws to est SP drop at 4000 fpm.
Anybody here have any data or experience on rectangular fitting pressure drop for my situation. I'm hesitant on using turning vanes at this velocity not just for SP drop but permanent deformation or blow-out.