rand1234
Electrical
- Jun 18, 2018
- 6
Hi Everyone,
Hope you all are doing well and thank you ahead of time for taking the time to read this post.
I wanted to get some feedback regarding arc horn versus non-arc horn design for high voltage air disconnects. Is there any industry standard/norm that dictates when arc horns should be installed for an air disconnect? All I have seen from one disconnect manufacturer is that if "very low levels" of resistive/magnetizing and capacitive currents exist during the operation of the switch, than arc horns are not required. This is pretty vague to me. Does this mean 1 amp, 2 amps, etc.?
The reason why I am asking is because vertical air disconnects equipped with arc horns require quite a bit more clearance phase to phase and phase to ground per IEEE 36.30.1. For example, taking the scenario I am looking into, recommended clearances for the 245kV max system voltage level @ 900kV BIL is 192 inches phase to phase and 152 inches phase to ground. This is in comparison to non-arc horn air disconnects which have a recommended clearance of 132 inches phase to phase and 80 inches phase to ground for the same system voltage.
I have actually measured the no load current in the location where I am evaluating the feasibility of installing a vertical air disconnect which is ~1.5 amps. Resistive/magnetization current is estimated at ~.37 amps based on transformer FAT reports and the rest is assumed to be capacitive. Due to clearance issues in my specific application, there is no way an air disconnect equipped with arc horns can be installed. Due to this, I am trying to determine whether a non-arc horn design would can be installed safely. I understand the reason why arc horns are installed and their benefit of diverting the arc from the main current carrying contacts. I wanted to get your guys' opinion based on your industry experience.
I appreciate any feedback anyone can provide. Thank you.
Hope you all are doing well and thank you ahead of time for taking the time to read this post.
I wanted to get some feedback regarding arc horn versus non-arc horn design for high voltage air disconnects. Is there any industry standard/norm that dictates when arc horns should be installed for an air disconnect? All I have seen from one disconnect manufacturer is that if "very low levels" of resistive/magnetizing and capacitive currents exist during the operation of the switch, than arc horns are not required. This is pretty vague to me. Does this mean 1 amp, 2 amps, etc.?
The reason why I am asking is because vertical air disconnects equipped with arc horns require quite a bit more clearance phase to phase and phase to ground per IEEE 36.30.1. For example, taking the scenario I am looking into, recommended clearances for the 245kV max system voltage level @ 900kV BIL is 192 inches phase to phase and 152 inches phase to ground. This is in comparison to non-arc horn air disconnects which have a recommended clearance of 132 inches phase to phase and 80 inches phase to ground for the same system voltage.
I have actually measured the no load current in the location where I am evaluating the feasibility of installing a vertical air disconnect which is ~1.5 amps. Resistive/magnetization current is estimated at ~.37 amps based on transformer FAT reports and the rest is assumed to be capacitive. Due to clearance issues in my specific application, there is no way an air disconnect equipped with arc horns can be installed. Due to this, I am trying to determine whether a non-arc horn design would can be installed safely. I understand the reason why arc horns are installed and their benefit of diverting the arc from the main current carrying contacts. I wanted to get your guys' opinion based on your industry experience.
I appreciate any feedback anyone can provide. Thank you.