cuky2000
Electrical
- Aug 18, 2001
- 2,133
Does any one know a methodology to derate a 230 kV disconnect switch rated for 3000 A continuous, 88 kA symmetrical SC current, 230 kV peak, and 142 kA asymmetrical.The switch should not be derated as a circuit breaker since will operate in close position during SC event with the following condition:
a) Magnetic Force: Driven by the peak current in approx. 1/4 of a cycle. The DC decay imposed by the X/R will not be significant with the short time.
b) Heating effect (I2R): Do not act instantaneous and driving by the RMS current. Since the switch is tested for 3 sec (180 cycles) and the protective device much shorter (let's say 18 cycles), by the time the switch component reach critical temperature, the circuit will be de-energize.
Please let us know your though regarding the impact of the X/R on disconnect switch rating.
a) Magnetic Force: Driven by the peak current in approx. 1/4 of a cycle. The DC decay imposed by the X/R will not be significant with the short time.
b) Heating effect (I2R): Do not act instantaneous and driving by the RMS current. Since the switch is tested for 3 sec (180 cycles) and the protective device much shorter (let's say 18 cycles), by the time the switch component reach critical temperature, the circuit will be de-energize.
Please let us know your though regarding the impact of the X/R on disconnect switch rating.