One of the 11 kV, 3000 kW, 2900 rpm motor was recently overhauled.
When the motor was sent back to site, they have conducted the motor solo run. The magnetic center of the rotor was found to be drifted.
Total axial free float of the motor is 13 mm. The magnetic center is expected to be at 6.5 mm from either end (i.e the mid point of 13 mm). This is an ideal case, which may not be the case in the actual scenario.
During the solo run (de-coupled running at location) the shaft was found to be travelled fully towards the driving End (DE). However with the slight adjustment in the leveling the rotor has moved towards the center. As it was a two pole machine, the magnetic pull being weak, the rotor was oscillating slightly. From this exercise, we can make out that the axial trust is not very high. So can we couple the motor with the pump by manually adjusting the rotor to the mid point of total axial float?
The motor was only overhauled, without any mechanical modifications. Hence we don’t find any reason which might have drifted the magnetic center of the motor.
This is a 28 years old motor. The condition of the stator is not very good. Can a drift in the magnetic center happen over the period time during the service?
While removing the motor for overhauling, the magnetic center was not tested and marked. Hence it is now not possible to ascertain whether the drift has taken place during the overhauling or it was developed before taking the motor out for overhaul, but not noticed or recorded.
Can you share your experience in this regard?
Also I would appreciate if you can give some practical solution or mitigation.
When the motor was sent back to site, they have conducted the motor solo run. The magnetic center of the rotor was found to be drifted.
Total axial free float of the motor is 13 mm. The magnetic center is expected to be at 6.5 mm from either end (i.e the mid point of 13 mm). This is an ideal case, which may not be the case in the actual scenario.
During the solo run (de-coupled running at location) the shaft was found to be travelled fully towards the driving End (DE). However with the slight adjustment in the leveling the rotor has moved towards the center. As it was a two pole machine, the magnetic pull being weak, the rotor was oscillating slightly. From this exercise, we can make out that the axial trust is not very high. So can we couple the motor with the pump by manually adjusting the rotor to the mid point of total axial float?
The motor was only overhauled, without any mechanical modifications. Hence we don’t find any reason which might have drifted the magnetic center of the motor.
This is a 28 years old motor. The condition of the stator is not very good. Can a drift in the magnetic center happen over the period time during the service?
While removing the motor for overhauling, the magnetic center was not tested and marked. Hence it is now not possible to ascertain whether the drift has taken place during the overhauling or it was developed before taking the motor out for overhaul, but not noticed or recorded.
Can you share your experience in this regard?
Also I would appreciate if you can give some practical solution or mitigation.