Hi Kalikot,
Not allowed. Keep the water (and possible condensation that goes along with it) out of the electrical rooms. If the room needs cooling, set your fan-coil unit outside the room and duct some cold air in.
NEC 110.26(F)(1) gives specifics.
Good on ya,
Goober Dave