I am evaluating existing foundation of 80ft tall vertical vessel. My calculations show that steel capacity of anchor bolts and concrete breakout strength of anchors in tension are NOT adequate to resist applied tension loads per the current codes. To make it work I am proposing FIELD DRILLING (16)~1-1/2"?x36" DEEP HOLES AND SETTING 1-1/4"? ALL THREADED RODS (HAS ASTM A193, GR. B7) WITH HILTI HIT-RE 500-SD ADHESIVE. To increase anchor’s effective embedment depth hef I am adding on top of existing fdn mat new concrete 12” thick doweled to the mat (see attached sketch).
However after running Hilti PROFIS Anchor program with hef=25in (max. approved) these anchors are still failing (concrete breakout 11% and pullout 8% - see attached Design Report from PROFIS).
Question: In order to increase anchors’ capacity can I use actual embedment of 30” with prorated capacity (multiply capacity with max. approved hef=25in from PROFIS by ratio 30/25=1.2)? Also I would like to use bigger diameter rod. Is this allowed since Hilti has data only up to 1-1/4”??
BTW I have called HILTI’s tech support with no luck.
Regards,
iv
However after running Hilti PROFIS Anchor program with hef=25in (max. approved) these anchors are still failing (concrete breakout 11% and pullout 8% - see attached Design Report from PROFIS).
Question: In order to increase anchors’ capacity can I use actual embedment of 30” with prorated capacity (multiply capacity with max. approved hef=25in from PROFIS by ratio 30/25=1.2)? Also I would like to use bigger diameter rod. Is this allowed since Hilti has data only up to 1-1/4”??
BTW I have called HILTI’s tech support with no luck.