7carisfast
Electrical
- Jun 15, 2004
- 48
We have a customer in Philly who currently has an old 2 Phase system (which history tells me has a phase shift of 90 Deg). These systems used to be popular in Philly and still existing in some areas. For years, the customer had what appears to be a single phase buck-boost transformer to turn their two phase system into a three phase system (solely for the purpose of a 3 phase HVAC on roof). The buck Boost phase is what they used to call a teaser leg to my knowledge and is commonly referred to as the Scott configuration. PECO did some line work and within 1 or 2 weeks, this single phase transformer blew. They purchased a 2 Phase to 3 Phase transformer from Federal Pacific, but upon checking the secondary, they measured 240,323 and 83V. Federal Pacific suggested replacing the new transformer with another new unit, but the results were the same. They were on the phone for literally for 3 hours providing onsite values.
It's of my opinion that PECO upgraded the system to a modern day system with a 120 Deg phase shift. No one in the area/block has issues as it's residential and they only have single phase services. Could this be the cause of the failed unit (besides age) and the bad readings from the new transformer(s)?
It's of my opinion that PECO upgraded the system to a modern day system with a 120 Deg phase shift. No one in the area/block has issues as it's residential and they only have single phase services. Could this be the cause of the failed unit (besides age) and the bad readings from the new transformer(s)?