Hi Supun93,
phamENG has great points, but to add to this topic, the shear walls are used to resist lateral loads on the structure due wind and/or seismic loads, and their capacity requirements, sizes, locations, and detailing need to determined based upon the structural shape and loads to be resisted. The requirements will also change based upon if you assume rigid or flexible diaphragm analysis if you are resisting seismic forces.
Generally speaking, hold downs will be required at each shear wall, unless the factored dead load from the ASCE 7-16 load combination (0.6DL + 0.7E) is large enough to resist the overturning force at the top of the wall due to shear loads. Because wood framed buildings tend to be light weight, without a significant amount of dead load, in my experience, it's rare to have a situation where the dead load overtop is sufficiently large to resist the overturning force, but that may be different in other parts of the US where wind design controls. Therefore, hold downs are usually specified at shear wall ends in my region.
There are different methods to determine shear walls, you can use the perforated or segmented methods, both of which are details in SDPWS as phamENG indicated. If you want to use Simpson Strong Walls, you'll need to perform a stiffness comparison between the strong wall and the other shear walls on the wall line to ensure that you are distributing lateral shear loads appropriately to each shear wall segment. Commentary to SDPWS provides an example of how to do this for different wall types, but additional analysis and derivation will be required for proprietary walls like those that Simpsons make.