I have a client that required ESFR protection in the RFP for a large warehouse with a maximum deck height of 38’-0”. I later found that part of their storage arrangement included open top five sided combustible containers on horizontal carousels with storage height at 8’-0”. The applicable building code is UFC 3-600-01 and the fire sprinkler code is NFPA 13, 2010. UFC 3-600-01 requires the use of FM data sheet 8-33 for protection of the carousel.
Does anyone have any suggestions for protection without the use of a horizontal sub ceiling at 3’ to 10’ above the carousel with sprinklers in the sub-ceiling, sprinklers above the sub-ceiling at the roof deck, and in-rack sprinklers in the carousel? (This is now a $250,000.00 change order they are trying to avoid)
The client has offered to switch to non-combustible five sided containers with holes punched in the bottoms of them to allow water to penetrate through to lower levels of storage but I am not sure if this meets the intent of the code. Can I still use the ESFR sprinklers above the carousel if they provide the previously mentioned non-combustible containers. Are they still considered “five sided” containers if they punch holes in the bottom of them. If yes how much would they have to punch out to make it acceptable 50%, 75%?. Any opinions/suggestions on this issue will be appreciated. Thanks.
Does anyone have any suggestions for protection without the use of a horizontal sub ceiling at 3’ to 10’ above the carousel with sprinklers in the sub-ceiling, sprinklers above the sub-ceiling at the roof deck, and in-rack sprinklers in the carousel? (This is now a $250,000.00 change order they are trying to avoid)
The client has offered to switch to non-combustible five sided containers with holes punched in the bottoms of them to allow water to penetrate through to lower levels of storage but I am not sure if this meets the intent of the code. Can I still use the ESFR sprinklers above the carousel if they provide the previously mentioned non-combustible containers. Are they still considered “five sided” containers if they punch holes in the bottom of them. If yes how much would they have to punch out to make it acceptable 50%, 75%?. Any opinions/suggestions on this issue will be appreciated. Thanks.