swoosh172
Mechanical
- Jan 8, 2008
- 49
Have you ever heard of horizontal heads not being within a wall cavity? We have a historic building where the client is requesting we do not install any piping in the walls. They also do not want the upright pendants in the middle of the ceiling, so they are requesting sidewall heads on exposed piping. What do you think? NFPA requires 4 inches max to the deflector, I can't find a head that would meet this.