OUe
Structural
- Feb 14, 2007
- 47
I'd like a consensus on whether horizontal joint reinforcement is used in SDC D,E,F for special reinforced masonry walls. I am a senior structural engineer and work for a jurisdiction performing plan review in Oregon. Many times we get designs from back East and I am questioning whether a recent East Coast engineering submittal for SDC, R=5, Bearing Wall Special Reinforced Masonry Shearwall should be allowed to be constructed with only horizontal joint reinforcement in lieu of bond beams. The engineer is certainly designing with partially grouted walls, which is fine in SDC D. However, all the partially grouted details are showing truss-type reinforcement for the horizontal shear. My question is 2 fold:
1)If by calculation, the masonry can take all of the shear, is horizontal joint reinforcement OK?
2)If by calculation, the steel takes all the shear but you believe joint reinf is ok in question 1, would you then consider rebar if steel takes all the shear? As many of you know, the ACI is written (last I checked) for either the masonry or the steel to take the shear exclusively.
ACI 530-11 section 1.18 says that the horizontal bars must have hooks around the vertical bars at wall terminations, so maybe I'm answering my own question...?
James Amrhein Link has written many publications where horizontal joint reinforcement is allowed around openings but it must still meet the requirements of 4' max 0.2 in^2 horizontal reinforcement for special masonry walls.
Thanks in advance for your comments.
1)If by calculation, the masonry can take all of the shear, is horizontal joint reinforcement OK?
2)If by calculation, the steel takes all the shear but you believe joint reinf is ok in question 1, would you then consider rebar if steel takes all the shear? As many of you know, the ACI is written (last I checked) for either the masonry or the steel to take the shear exclusively.
ACI 530-11 section 1.18 says that the horizontal bars must have hooks around the vertical bars at wall terminations, so maybe I'm answering my own question...?
James Amrhein Link has written many publications where horizontal joint reinforcement is allowed around openings but it must still meet the requirements of 4' max 0.2 in^2 horizontal reinforcement for special masonry walls.
Thanks in advance for your comments.