Horizontal Reinforc'g in Masonry Walls

Status
Not open for further replies.

mdale

Structural
May 12, 2003
14
Are the requirements for the minimum horizontal steel (0.007Ag)in a masonry wall for wind design the same as for seismic loading. I looking at a masonry wall in 130-mph wind speed.
 
Replies continue below

Recommended for you

Looks like your wind pressure would generates a reaction high enough to push you beyond the minimum requirement, unless you stick to one way design.
 
I am curious as to which code requires .007Ag horizontal reinforement in masonry walls. That is a lot of reinforcement, and it must be for seismic loading. Wind loading normal to walls is usually taken by one way bending between floors, with only a nominal amount of horizontal reinforcing. A greater amount of horizontal reinforcement is often required in shear walls of multistorey buildings, but that doesn't come under "minimum requirements".
 
There's a digit missing in the number. It's .0007Ag for Seismic Class D and above in ACI 530-02 1.13.5
 
In that case, that is not much reinforcement, but is about twice the amount some codes prescribe for "secondary reinforcement" in reinforced masonry.
 