RE: APA Table: Diaphragms: Recommended Shear for Horizontal APA Panel Diaphragms ...
We need to analyze the load applied to both the length and width of sheathing.
"Case 1" represents the sheathing layout I use, but there does not seem to be a corresponding Case with the load parallel to, and the framing perpendicular to the sheathing length. Until a year ago, I had considered "Case 3" to be that particular Case. Then someone pointed out that, the word "Framing" is pointing to the line parallel to the sheathing length. If this is correct, then the width of the sheathing is spanning 48". With the exception of "Case 3", all the other Cases have the framing at 24" oc and perpendicular to sheathing length. I think "Case 3" is an error. I believe the word "Framing" is actually pointing to Blocking.
Any thoughts or comments?
Thank you!
We need to analyze the load applied to both the length and width of sheathing.
"Case 1" represents the sheathing layout I use, but there does not seem to be a corresponding Case with the load parallel to, and the framing perpendicular to the sheathing length. Until a year ago, I had considered "Case 3" to be that particular Case. Then someone pointed out that, the word "Framing" is pointing to the line parallel to the sheathing length. If this is correct, then the width of the sheathing is spanning 48". With the exception of "Case 3", all the other Cases have the framing at 24" oc and perpendicular to sheathing length. I think "Case 3" is an error. I believe the word "Framing" is actually pointing to Blocking.