dg47
Civil/Environmental
- Dec 5, 2008
- 5
I have a question on the blowdown from 3 hot lime softeners at a facility. I'm a wastewater consultant. For environmental reasons, we intend to capture and dewater the lime solids from the softeners. The blowdown is at 22 psi and 230F. About a 10% lime slurry. There is a continuous blowdown of 100 gpm from the combined units or about 60,000 lb/h. The solids will be separated in a thickener tank and the overflow of soft water will be recycled back to the system. Do I need a flash tank before the thickener? I think so; however, I have an purge blowdown that can be quite high for 20-30 seconds from a 6" pipe wide open every couple hours. The flash tank would be very large if I have to size for the high purge. Any suggestions? Thank you.