Hypothetically...
I have a "boiler" (which started off in design as a "heat medium heater" until the heat medium conditions required it to become a "boiler") that supplies water/glycol as heat medium. It is classified as a high-temperature water boiler per ASME Section I: - no way around it.
PG-61.1 states, in part:
"Except as provided for in PG-61.3, PG-61.4 and PG-61.5, each source of feeding shall be capable of supplying water to the boiler at a pressure of 3% higher than the highest setting of any safety valve on the boiler."
PG-61.4 states:
"High-temperature water boilers shall be provided with means of adding water to the boiler or system while under pressure."
As fate would have it, PSVs on the *new* "boiler" are set at a setting significantly higher than the shut-off pressure that can be developed by the *existing* centrifugal feed pumps, so that in the present system, compliance with PG-61.4 is possibly achieved, but full compliance with PG-61.1 (wrt water supplied at 103% of SP) is certainly not achieved.
My question is, does PG-61.4 supersede and relax PG-61.1 for this particular issue in this instance, or is a modification required in one or the other of:
(1) Pump upgrade to achieve the 103% of SP on PSVs;
(2) Change boiler PSV settings to lower than existing feed pump shut-off pressure?
I am unclear as to the correct interpretation, and I would appreciate some input before taking it up with our Regulatory body.
Regards,
SNORGY.
I have a "boiler" (which started off in design as a "heat medium heater" until the heat medium conditions required it to become a "boiler") that supplies water/glycol as heat medium. It is classified as a high-temperature water boiler per ASME Section I: - no way around it.
PG-61.1 states, in part:
"Except as provided for in PG-61.3, PG-61.4 and PG-61.5, each source of feeding shall be capable of supplying water to the boiler at a pressure of 3% higher than the highest setting of any safety valve on the boiler."
PG-61.4 states:
"High-temperature water boilers shall be provided with means of adding water to the boiler or system while under pressure."
As fate would have it, PSVs on the *new* "boiler" are set at a setting significantly higher than the shut-off pressure that can be developed by the *existing* centrifugal feed pumps, so that in the present system, compliance with PG-61.4 is possibly achieved, but full compliance with PG-61.1 (wrt water supplied at 103% of SP) is certainly not achieved.
My question is, does PG-61.4 supersede and relax PG-61.1 for this particular issue in this instance, or is a modification required in one or the other of:
(1) Pump upgrade to achieve the 103% of SP on PSVs;
(2) Change boiler PSV settings to lower than existing feed pump shut-off pressure?
I am unclear as to the correct interpretation, and I would appreciate some input before taking it up with our Regulatory body.
Regards,
SNORGY.