Hot water pipe insulation

Status
Not open for further replies.

R22Tailrotor

Electrical
Oct 20, 2001
4
0
0
US
I need some help on calculating the insulation specifications on a domestic hot water re-circulating system. I have 200 feet of 3/4 inch copper pipe. Can the insulation be specified based on a heat loss that is a percentage of the hot water used. In other words insulate so that perhaps 5% of the heat is lost in the pipes so the efficiency of the system would be 95%. The system circulates all day but the hot water is used sporatically. I would guess about 100 gallons of hot water are used daily.

Bill
 
Replies continue below

Recommended for you

calculate the heat loss in BTUH, based on system temperature, ambient conditions, and insulation characteristics. 3/4-inch copper pipe is generally provided with 1-inch thick fiberglass insulation. Depends of course on application. Then, calculate heat loss to determine appropriate recirculation rate etc.
 