I just want to better my understanding of pump/system curves.
Am I right in my thinking about this? If I put an automatic flow control valve (like a Griswold) into a system as a main balancing valve, it would appear as a vertical line on the system curve, correct? I threw together a chicken-scratch sketch (see attached). With no Griswold, my system curve follows a basic quadratic shape and intersects the pump curve. I pulled numbers out of the air, so let's say that point is 1,200 GPM @ 50' of head.
Now let's say I insert a Griswold that is sized for 1,000 GPM over a delta-P range of 12'-75', So, won't my system resistance curve follow the quadratic until I get to 1,000 GPM, then it will turn vertical until it intersects the pump curve? So my operating point to 1,000 GPM and let's say that corresponds to 60' of head.
So finally, if I just used a regular circuit setter valve instead of a Griswold, I would just get a new steeper quadratic curve that passes through 1,000 GPM @ 60', correct?
Am I right in my thinking about this? If I put an automatic flow control valve (like a Griswold) into a system as a main balancing valve, it would appear as a vertical line on the system curve, correct? I threw together a chicken-scratch sketch (see attached). With no Griswold, my system curve follows a basic quadratic shape and intersects the pump curve. I pulled numbers out of the air, so let's say that point is 1,200 GPM @ 50' of head.
Now let's say I insert a Griswold that is sized for 1,000 GPM over a delta-P range of 12'-75', So, won't my system resistance curve follow the quadratic until I get to 1,000 GPM, then it will turn vertical until it intersects the pump curve? So my operating point to 1,000 GPM and let's say that corresponds to 60' of head.
So finally, if I just used a regular circuit setter valve instead of a Griswold, I would just get a new steeper quadratic curve that passes through 1,000 GPM @ 60', correct?