How are UPS SC Contributions estimated? 2

Status
Not open for further replies.

Wfg42438

Electrical
Apr 10, 2017
70
Hello Everyone,

In power system softwares i have seen that the UPS SC contributions are modeled by multiplying the FLA rating times a fixed multiplying factor.

I have seen this done to estimate the UPS SC contribution for the AC and DC outputs of the UPS.

I was wondering if anyone can shed some light on where this multiplying factor comes from?

Is this from the manufacturer or is this a rule of thumb from a standard or document perhaps?

I dont have a specific application in mind i just want to get a better understanding on how the UPS is modeled during a SC.
 
Replies continue below

Recommended for you

I don't usually use the presets in the software and get the info from the OEM. But also, since a UPS can only provide a relatively small amount of SC current (related to its source) before transferring to bypass to clear the downstream fault, I typically don't worry about it.

Mike

i.e. just model the system in bypass.
 
You have to ask the manufacturer.
It depends on the amount of short time overload is allowed and/or if motor starting is provided for.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
Thank you for the feedback

are there any sample data sheets anyone would be willing to share so i can see how the data is typically shown by a manufacturer?
 
Thank you for sharing these documents this is what I needed!
 