BruceVan
Chemical
- Oct 10, 2003
- 1
In relief valve analysis, one contingency is blocked outlets. This scenario consideres the outlet valve closed with process supply pressure on the inlet. If incoming pressure exceeds MAWP (or a lower pressure if other considerations require it), then relief protection must be provided. What I don't understand is the API 521 statement under section 3.5 Closed Outlets.
API states, "In the case of heat exchangers, a closed outlet can cause thermal expansion or possibly vapor generation." My understanding of heat exchanger operation, particularly on cooling water side, is that if only the outlet is closed, the inlet remains open and any thermal expansion will disperse through the open inlet. This would not produce a relief case.
When both the cold side inlet and outlet valves are blocked, a thermal expansion case is considered.
Can someone explain the reasoning behind the API 521 statement that closing the outlet valve with the inlet open can cause thermal expansion?
API states, "In the case of heat exchangers, a closed outlet can cause thermal expansion or possibly vapor generation." My understanding of heat exchanger operation, particularly on cooling water side, is that if only the outlet is closed, the inlet remains open and any thermal expansion will disperse through the open inlet. This would not produce a relief case.
When both the cold side inlet and outlet valves are blocked, a thermal expansion case is considered.
Can someone explain the reasoning behind the API 521 statement that closing the outlet valve with the inlet open can cause thermal expansion?