lisah
Industrial
- Dec 8, 2003
- 2
Hi.
Apologies in advance for a basic question. Although my background is mathematics, I have very little electrical knowledge so please bear with me!
My factory runs on a 3-phase power supply of 415 volts. In addition, if all our machines were to run at once, the maximum load demand is 260kw.
My understanding is that this equates to 330kva (assuming 80% power for constant supply). With a 3-phase system does this mean we need a minimum of a 460amp supply?
[3ø, Amps = (kVA*1000)/Volts/1.732 (SqRoot of 3)]
I know that there is a 600amp cable from the mains supply in the street which at present changes to a 300amp cable into our building. Would it make sense to arrange for an upgrade to the full 600amp supply? If this is the case, then is this equivalent to requesting a service availability of 500kva?
Any help would be appreciated!
Lisa