The Plant I'm working for just adopted this new standard even though it's a couple years old.
And I'm running into this common situation: The short circuit current at some 208V disconnect switches is only like 300A, and on its upstream molded case circuit breaker it times out to the 2 sec max - and the calculation gives a high incident energy.
But then you've got this exception - under 2000A SCA, it won't sustain an arc....What does your Plant put on the labels ? 0.0 Incident Energy? or NO ARC FLASH HAZARD? What if you get a low energy number anyway by the standard method? Say like 0.5 cal^cm2 , do you use that or is it really NO ARC FLASH HAZARD?
And I'm running into this common situation: The short circuit current at some 208V disconnect switches is only like 300A, and on its upstream molded case circuit breaker it times out to the 2 sec max - and the calculation gives a high incident energy.
But then you've got this exception - under 2000A SCA, it won't sustain an arc....What does your Plant put on the labels ? 0.0 Incident Energy? or NO ARC FLASH HAZARD? What if you get a low energy number anyway by the standard method? Say like 0.5 cal^cm2 , do you use that or is it really NO ARC FLASH HAZARD?