bdn2004
Electrical
- Jan 27, 2007
- 794
I'm trying to model this tie breaker that's on a 13.8kV system tying the two switchgear busses together. And to see if the settings make sense. It has a relay but I don't know how the CT's are connected. on both sides? This particular tie in the pick is set to 1200A and a 5 sec time delay, it TCC plots the same as the main but offset by 200A less.
I can see 6 scenarios with this tie breaker: 1) Open, both sources energized, 2) Open, one source energized, 3) Open , the other source energized, 4) Closed both sources energized 5) Closed one source energized 6) Closed the other source energized. I was going to pick the worst case scenario for an arc flash determination. Is this the way this is generally done?
I can see 6 scenarios with this tie breaker: 1) Open, both sources energized, 2) Open, one source energized, 3) Open , the other source energized, 4) Closed both sources energized 5) Closed one source energized 6) Closed the other source energized. I was going to pick the worst case scenario for an arc flash determination. Is this the way this is generally done?