ME27272727
Mechanical
- May 15, 2014
- 88
My experience with chilled water economizer has been with inducted-draft counter-flow open towers in hospitals where we are able to reset the chilled water temperature upwards towards 50°F to get the approach needed to run free cooling with a 42°F min condenser water temp. The big name tower manufacturer's seem to recommend 40-42F as a minimum tower leaving water temp in order to prevent icing up the towers.
I'm currently analyzing a free cooling opportunity for a process chilled water application where 40F CHWS temp is required year round. Has anyone had success running towers down to perhaps 36F? There is big potential for savings, but the lower CHWS temp is hamstringing me.
I'm currently analyzing a free cooling opportunity for a process chilled water application where 40F CHWS temp is required year round. Has anyone had success running towers down to perhaps 36F? There is big potential for savings, but the lower CHWS temp is hamstringing me.