davefao,
The steepness of the pump curve is not necessarily much of an issue, but it is usually important that the head vs. flow curves rise continuously to shut-off (zero flow). This is significant for stable operation and start-up.
With a system such as you describe, I would want to have good tachometers on both pump shafts to be sure that they are both operating at suitable speeds. (If the pumps are identical, then the pump shaft speeds usually should be kept identical.) It is far too easy for one pump to hog the load if the shaft speeds do not match very closely. The turbine's governor speed droop characteristics vs. the motor slip characteristics can lead to significant differences in shaft speeds between the two pumps.
I would carefully review the system head vs. flow characteristics and the pump curves. I would want to eliminate the orifices if at all possible. Any lack of symmetry in the pump-specifc piping should be carefully considered for the effects that would tend to cause unequal flow through the pumps.
To this point, I've been assuming two identical pumps. If the pumps are not identical, then I would want to include flow rate measurement for each pump in the control system to assure that both pumps remain suitably loaded at all times.
You have an interesting problem with the possibility of introducing significant energy and maintenance savings. Good luck!