musaUKPN
Electrical
- Jul 25, 2011
- 22
I am involved in design of a new supply for a commercial building. The building will have supplies from two different sources each coming from different 132/11kV utility substations.
Supply-1 will be fed @ 400volts 3-phase from utility source-1 via dedicated 1MVA 11kV delta / 0.433 kV Y transformer (Z=4.5%). The transformer will be installed inside the building along with 11kV switches and is owned by utility but it will supply our building only. The utility solidly grounds the Y connected secondary and provide 3-phase + neutral supply to the building. They also provide earth terminal if certain conditions are fulfilled. Supply-1 is for the main building use (facilities, office, parking, etc) except for the two shops on the ground floor of the building which are fed via supply-2. The expected peak load for supply-1 will be 810kVA.
Supply-2 will be @ 400volts 3-phase from utility source-2 via a utility distribution transformer. The utility distribution transformer is in another nearby building around 300 meters away and it supplies multiple customers. The shops in our building will be supplied via two 3-phase+ PE (combined neutral & earth) service cables (each rated 100A). These two services will be PME (protective multiple earth). The expected peak load for supply-2 will be 130kVA (65kVA each service). The utility also solidly grounds their distribution transformer and provides PME supplies to all customers.
The rough value for the utility and dedicated transformer earthing is less than 1 ohm. The earth loop impedance limit for the two PME services is less than 0.35 ohm. The utility provided 3-phase & SLG fault values (max & min) are given. I have attached schematics for your understanding with all values.
My questions are:
1. How can we calculate Earth potential rise (EPR)?
2. How we calculate touch potential?
3. What are the best ways to arrange earthing/ bonding at above site? Shall I consider single earthing for both the supplies or two separate earths?
Your comments will be highly appreciated.
Please let me know if more information/ data is required.
Supply-1 will be fed @ 400volts 3-phase from utility source-1 via dedicated 1MVA 11kV delta / 0.433 kV Y transformer (Z=4.5%). The transformer will be installed inside the building along with 11kV switches and is owned by utility but it will supply our building only. The utility solidly grounds the Y connected secondary and provide 3-phase + neutral supply to the building. They also provide earth terminal if certain conditions are fulfilled. Supply-1 is for the main building use (facilities, office, parking, etc) except for the two shops on the ground floor of the building which are fed via supply-2. The expected peak load for supply-1 will be 810kVA.
Supply-2 will be @ 400volts 3-phase from utility source-2 via a utility distribution transformer. The utility distribution transformer is in another nearby building around 300 meters away and it supplies multiple customers. The shops in our building will be supplied via two 3-phase+ PE (combined neutral & earth) service cables (each rated 100A). These two services will be PME (protective multiple earth). The expected peak load for supply-2 will be 130kVA (65kVA each service). The utility also solidly grounds their distribution transformer and provides PME supplies to all customers.
The rough value for the utility and dedicated transformer earthing is less than 1 ohm. The earth loop impedance limit for the two PME services is less than 0.35 ohm. The utility provided 3-phase & SLG fault values (max & min) are given. I have attached schematics for your understanding with all values.
My questions are:
1. How can we calculate Earth potential rise (EPR)?
2. How we calculate touch potential?
3. What are the best ways to arrange earthing/ bonding at above site? Shall I consider single earthing for both the supplies or two separate earths?
Your comments will be highly appreciated.
Please let me know if more information/ data is required.