Dear all
i have an electric generator of 100kva,3 phases and i need to know how much amperes i have on each phase and also how much should i use in nominal consumption
 
Replies continue below

Recommended for you

You should know the generator rated voltage V.

Then your rated line current = (100 x 1000)/(1.732 x V)

 
The maximum current depends on the heating effect and is stated by the manufacturer. Depending on the service, (Prime, Standby, Continous) the manufacturer may assign different maximum current ratings to the same generator.
Maximum current will be given on the nameplate.
Note that if a generator rated at 208 volts is used at 240 volts, the KVA rating will increase. The maximum allowable current will be the same.
With this in mind, use edison123's formula with rated voltage.
respectfully
 