Ben9108
Civil/Environmental
- May 9, 2006
- 4
A below chiller was serving for a building. In order to achieve energy saving, one fan coil unit was switched off.
Cooling Capacity of Chiller (Kw): 347
Electricity Consumption of Chiller (KWH): 117.485
Operating Current of Chiller (A): 210
COP of chiller: 2.95
Cooling Capacity of Fan coil unit (KW): 6.8
I would like to seek someone help for assessing the below calculation for energy saving.
(347-6.8)/2.95 = 115.322KWH
Saving for Electricity Consumption of chiller = 117-115.322 = 2.163KWH