how to calculate the fault current on D/Yd Tx D side, if Y side has ground fault? 2

Status
Not open for further replies.

davidy51

Electrical
Feb 25, 2022
1
0
0
CA
if there is a 20Mva, 35kV/4.16kV, 5%z Tx with D/Yd winding configuration.
if 4.16kV side has single A phase ground fault, theoretically how much is the 35kV side current? on which phase?
 
Replies continue below

Recommended for you

All of the fault current will be in one winding on both sides of the transformer. If you know the Y side current, you can just use the turns ratio between the windings to calculate the current in the one delta winding. Remember to use the line to neutral voltage when determining the turns ratio. Current will be in whatever delta winding corresponds to the secondary A-phase winding. So you'll have current in two phases on the primary side.
 