jochav52802
Structural
- Nov 28, 2018
- 81
I'm working on a project where we need to add a new concentrated load to an existing 6" overall slab on 3" metal deck.
I contacted the Steel Deck Institute (SDI) with a sketch and dimensions of the underside of the deck, and was told definitively that since there are no visible embossments, the deck is a non-composite deck.
I then computed the maximum positive moment based on the dead and live loads specified in the original general notes drawings as well as based on the (2) live load patterns specified in ACI 318-14.
Next, I computed the positive moment capacity based on ACI 318-14 and determined that the slab alone had no where near the amount of capacity required to support the existing loads without some sort of composite action.
Any thoughts on how I might go about verifying the true capacity of the floor? Does it make any sense to take the original dead and live loads, pattern them per ACI 318-14, and use the resulting maximum positive and negative moments as a basis for what the floor was designed for?
The design live load was 100 psf, and I'm thinking of de-rating that value for the client in order to accommodate the new concentrated loads. This is a an office space, which per ASCE 7-16, only requires a live load of 50 psf, so I'm thinking that I can potentially de-rate the floor by as much as 50 psf to make the new concentrated loads work.
Any thoughts or ideas are much appreciated, thank you!
I contacted the Steel Deck Institute (SDI) with a sketch and dimensions of the underside of the deck, and was told definitively that since there are no visible embossments, the deck is a non-composite deck.
I then computed the maximum positive moment based on the dead and live loads specified in the original general notes drawings as well as based on the (2) live load patterns specified in ACI 318-14.
Next, I computed the positive moment capacity based on ACI 318-14 and determined that the slab alone had no where near the amount of capacity required to support the existing loads without some sort of composite action.
Any thoughts on how I might go about verifying the true capacity of the floor? Does it make any sense to take the original dead and live loads, pattern them per ACI 318-14, and use the resulting maximum positive and negative moments as a basis for what the floor was designed for?
The design live load was 100 psf, and I'm thinking of de-rating that value for the client in order to accommodate the new concentrated loads. This is a an office space, which per ASCE 7-16, only requires a live load of 50 psf, so I'm thinking that I can potentially de-rate the floor by as much as 50 psf to make the new concentrated loads work.
Any thoughts or ideas are much appreciated, thank you!