Just want to make sure that I am looking at the right thing. Protection relay output contact spec says the following:
Make & Break Capacity:
DC: 50 W resistive
DC: 62.5 W inductive (L/R = 50 ms)
AC: 2500 VA resistive (cos φ = unity)
AC: 2500 VA inductive (cos φ = 0.7)
I assume that if circuit breaker trip coil has a burden of >62.5 W then we need to use either trip relay or protection relay with high make/break contacts such as the following:
Make & Break Capacity:
DC: 7500 W resistive
DC: 2500 W inductive (L/R = 50 ms)
Make & Break Capacity:
DC: 50 W resistive
DC: 62.5 W inductive (L/R = 50 ms)
AC: 2500 VA resistive (cos φ = unity)
AC: 2500 VA inductive (cos φ = 0.7)
I assume that if circuit breaker trip coil has a burden of >62.5 W then we need to use either trip relay or protection relay with high make/break contacts such as the following:
Make & Break Capacity:
DC: 7500 W resistive
DC: 2500 W inductive (L/R = 50 ms)