power2engineer
Electrical
- May 18, 2003
- 53

The Main switchboard is 13.KV S&C Fusible disconnect switch with Source Transfer controller for Manual OR Automatic Transfer scheme
I have 13.8 KV Grounded - WYE Utility incoming Power on main distribution switchgear.
On site Generator is 480V/277V WYE Stepped up to 13.8KV using 480/277V WYE-13.8KV Delta Transformer.
The S & C SOURCE TRANSFER CONTROLLER is supplied 3 Phase control voltage from voltage sensing VTs on Source sides of Utility & Em.Generator disconnect switches.
The STC essential looks for loss of Source 1 (Utility) and corresponding Switch Open condition to allow closing of Source 2 (Em.Gen.) Switch Manually or Automatically.
THE PROBLEM Em.Generator source coming from Delta winding of 480/277-13.8KV Step up transformer there is no reference ground for Em.Generator votage and the S & C STC does not work
because it is looking for voltage similar to Utility transformer.
How to provide the same ground reference to Em Generator 3 phase power(voltagees) as Utility 3 Phase Power ?