how to remove moisture from medium voltage motor?

Status
Not open for further replies.

emadshaaban

Electrical
Nov 2, 2011
59
dear sir
2.6MW 6.6KV induction motor ,gives low resistance with 4Mohm and was tripping with earth fault current (with fault current=42Amp),the network neutral connected to ground through 150 ohm resistor.
and because no signs of any winding damage ,we decide to condensate the winding to remove any humidity if located,
so we going to connect small power supply (400v) to the winding resistor(which rated with 6.6Kv) and the rotor was removed ,is this method correct?
 
Replies continue below

Recommended for you

Information on what to do after water damage
faq237-1157



"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> faq731-376
 
Thanks for the links jraef. These would really be helpful.
 
Does the motor have space heaters - can these be used?

Contact the manufacturer, I have seen atmospheric moisture drying proceedure in some IOM's.

I propose an inspection by a suitable person for other than atmospheric moisture.

Regards,
Lyle
 