How to terminate a cable bigger than maximum terminal size?

Status
Not open for further replies.

Power0020

Electrical
Jun 11, 2014
303
A VFD wiht a maximum cable size of 120 sq.mm, but due to the installation being a bit far from panel, a 185 sq.mm cable is needed, I wonder how can I fit these cable terminals? should extension bus be installed on the VFD terminals to handle these big lugs?
 
Replies continue below

Recommended for you

Transition box (junction box) close to the drive? Or a cast resin / heatshrink / coldshrink joint in the first few yards of cable?

If you are right out on the distance limit have you considered whether the drive needs filters to work properly?
 
See if one of these will help:
Link
These will drop your size about 2 AWG sizes.

Bill
--------------------