I have a question regarding let-trhough curves of fuses and circuit breakers. I have researched this forum but not found any thread that exactly addresses the question I have. Consider the attached pdf.
The top let-through curve is that of a fuse. We are dealing with a 80A fuse and the prospective fault current is 30kA. According to these curves, the fuse limits the rms fault current to around 6kA which is 8.4kA peak. Thus the current limiting (CL) action of the fuse allows the downstream network to be designed to 6kA and not 30kA.
The bottom curves are those for Schneider NSX range of CL breakers. Schneider, like most LV breaker manufacturers, provide cascading curves where the CL action and let-through energy allows for lesser rated cb’s downstream than the prospective fault level at the downstream location.
So let’s say I have a cascading combination in place, breaker A upstream and lower rated breaker B downstream. What should the fault rating of the cable between them be? Let’s say I have a NSX630A breaker upstream, Iprospective = 100kA. If the peak let-through is 46kA does that mean the rms let-through is 46/1.414 = 32.5kA? So my cable only need be rated for up to 32.5kA and not 100kA? Is this correct?
I am aware that there are let-through energy curves for CL cb’s as well but I have no idea if they’re any use when it comes to determing the reduced symmetrical fault current due to the action of the CL breaker.
Am keen to hear some thoughts regarding how to use these cb let-through curves to determine the reduced symmetrical fault current, if indeed this can be done!
The top let-through curve is that of a fuse. We are dealing with a 80A fuse and the prospective fault current is 30kA. According to these curves, the fuse limits the rms fault current to around 6kA which is 8.4kA peak. Thus the current limiting (CL) action of the fuse allows the downstream network to be designed to 6kA and not 30kA.
The bottom curves are those for Schneider NSX range of CL breakers. Schneider, like most LV breaker manufacturers, provide cascading curves where the CL action and let-through energy allows for lesser rated cb’s downstream than the prospective fault level at the downstream location.
So let’s say I have a cascading combination in place, breaker A upstream and lower rated breaker B downstream. What should the fault rating of the cable between them be? Let’s say I have a NSX630A breaker upstream, Iprospective = 100kA. If the peak let-through is 46kA does that mean the rms let-through is 46/1.414 = 32.5kA? So my cable only need be rated for up to 32.5kA and not 100kA? Is this correct?
I am aware that there are let-through energy curves for CL cb’s as well but I have no idea if they’re any use when it comes to determing the reduced symmetrical fault current due to the action of the CL breaker.
Am keen to hear some thoughts regarding how to use these cb let-through curves to determine the reduced symmetrical fault current, if indeed this can be done!