bdn2004
Electrical
- Jan 27, 2007
- 794
Attached in a manufacturer's drawing of a line reactor that is found on the supply fan of an HVAC unit at a plant where we are doing an arc flash evaluation.
I'd like to show this in series with the VFD. T
The program we are using has these parameters to fill in for a reactor:
1) Ampacity (225, 600, 1000,....6000)
2) Impedance kVA (3-phase)
and then it calculates the ohms from these numbers. btw this is a 480v, 3 phase, 50Hp motor. This line reactor says it's 65A on the nameplate.
The manufacturer told me this unit is 295 microhenries impedance.
I tried this: (480V)(65A)(1.732) = 54kVA. The program says the impedance in ohms from that is X1 = 0.018 , X0 = 0.018 and X/R is 18.9812
I'm not seeing 295 microhenries. Where am I screwing up?