CobusvanJ
Mechanical
- Dec 6, 2008
- 45
Hi,
Our client, a power station operator, has requested us to repair their HP Heaters. Wall thickness measurements have shown the shell to be very thin (13mm) in an 1m x 0.7m area, and on the heads.
They have stated that we should do a weld overlay on the thin area, but I am not so sure about the solution, especially being 0.7m^2 in area which in my opinion will lead to excessive heat input into the shell.
A second option would be to cut out the affected area and replace it with a rectangular section. My investigations into this proposed solution thus far has not shown any HP Heaters to have been repaired in this way, only LP Heaters.
Third option, which in my opinion is the only solution, is to cut out the whole affected strake, and replace with a new one.
Can anyone please advise on what methods of repair are allowable?
HP Heater Data:
Shell Side
Design Pressure -1/22 bar
Design Temperature 420deg C
Diameter 2100 mm
Length 9450mm
Starting wall thickness 20 / 40 mm
Material 15Mo3 / 17Mn4
Our client, a power station operator, has requested us to repair their HP Heaters. Wall thickness measurements have shown the shell to be very thin (13mm) in an 1m x 0.7m area, and on the heads.
They have stated that we should do a weld overlay on the thin area, but I am not so sure about the solution, especially being 0.7m^2 in area which in my opinion will lead to excessive heat input into the shell.
A second option would be to cut out the affected area and replace it with a rectangular section. My investigations into this proposed solution thus far has not shown any HP Heaters to have been repaired in this way, only LP Heaters.
Third option, which in my opinion is the only solution, is to cut out the whole affected strake, and replace with a new one.
Can anyone please advise on what methods of repair are allowable?
HP Heater Data:
Shell Side
Design Pressure -1/22 bar
Design Temperature 420deg C
Diameter 2100 mm
Length 9450mm
Starting wall thickness 20 / 40 mm
Material 15Mo3 / 17Mn4