cme

Mechanical
Jan 16, 2003
196
I am reviewing a set of plans for a hospital boiler plant in PA. The existing boilers are being replaced by a Contractor. There are 3-400bhp-150lb Cleaver Brooks 4-pass boilers connected to a 8"HPS header.

For each boiler there is a stop/check valve on the outlet, ATC valve, short length of pipe then an elbow, then a straight pipe section with a orifice and meter, then a stop valve at the header.

My questions are:

Is it permissible per ASME Sec 1 to put the atc valve and orifice meter between the stop/check and stop valve. The piping between them has to be welded by ASME qualified welders. I haven't seen a detail yet showing a free blowing drain valve per ASME Sec 1 between the stop/check and stop.

I can't think of a reason to put a ATC valve there.

They indicate 2 separate bottom blowdown assemblies complete with quick and slow opening valves. Why 2?

Are blowdown separators or tanks permissible with current codes?

Its been a while since I put in a HP boiler plant.

 
Replies continue below

Recommended for you

In many jurisdictions, the piping you're asking about would fall under ASME B31.1. And what'a an "ATC" valve?
 
sorry ...... "automatic temperature control" jargon which in this case is a 2 port control valve

just for laughs ..... I'd like to see the size actuator on that valve, 6" pipe I believe
 
What pressure will these boilers operate? If they're firing to maintain a header pressure of 125 PSIG, then you're likely looking at something like a 4" stop & check.

Why would a temperature control valve be required in the steam lead?

From the way you're describing things, I suspect that your high pressure steam boiler project is being handled by an outfit that normally does commercial hot water systems.
 