CuriousElectron
Electrical
- Jun 24, 2017
- 187
Greetings,
I have a question - suppose I have a station service transformer, 15kV delta connected on the primary and 480/277V Y connected on the secondary, supplying an MCC. The MCC is a 3 phase, 4 Wire system, but supplies only three phase, 3 wire loads. From design perspective, would there still be a benefit of high resistance grounding the neutral point of the Y-connected secondary of the transformer, if the service continuity is desired? My thought is that for 3 phase, 3 wire load, if one phase faults to ground at the load side, EGC would carry the ground fault current back to the switchgear ground bus and from MCC the fault current would flow back into the transformer.
I understand there are also other considerations, like safety and arc flash factors, but it may make sense to have delta connected secondary if service continuity is desired like in this scenario.
Am I on the right path with my reasoning?
Thank you,
EE
I have a question - suppose I have a station service transformer, 15kV delta connected on the primary and 480/277V Y connected on the secondary, supplying an MCC. The MCC is a 3 phase, 4 Wire system, but supplies only three phase, 3 wire loads. From design perspective, would there still be a benefit of high resistance grounding the neutral point of the Y-connected secondary of the transformer, if the service continuity is desired? My thought is that for 3 phase, 3 wire load, if one phase faults to ground at the load side, EGC would carry the ground fault current back to the switchgear ground bus and from MCC the fault current would flow back into the transformer.
I understand there are also other considerations, like safety and arc flash factors, but it may make sense to have delta connected secondary if service continuity is desired like in this scenario.
Am I on the right path with my reasoning?
Thank you,
EE