Please forgive me, I do not have a lot of experience with AASHTO...
I have a project that involves an exterior elevated driveway over the first story of a building (HS-20 loading). The driveway consists of a radiant heated concrete deck (7-9" depth) on top of high density rigid insulation (4" min), waterproofing membrane, supported by a structural reinforced concrete deck on 1-1/2" inverted composite decking. The driveway is supported by wide flange structural steel beams spaced 5 ft. on center, parallel with the "traffic" lanes. Girders are spaced every 30 ft. perpendicular to the drive lanes.
I believe I need to consider two loading conditions: 1. (Max tire load) 16 kip point load (10"x20" contact area), and 2. (Lane loading) A 640 lb/ft uniform load plus 18 kip and 26 kip point loads for maximum moment and shear distributed over a 10 ft. length. I do not think the lane loading will control in this case. I found a reference that the effective width "B" of slab used for design can be taken as B = 4 + 0.06*L (ft.) where L is the center to center spacing of supports. In my case, L is 5 ft., so B is equal to 4.3 ft. Seems reasonable, but that is quite a bit wider than the tire contact, so I'm not sure if it is conservative. I also assume you need to follow the AASHTO load factors for DL and LL with impact considered instead of ACI load factors in this case.
This is a bit tricky as its a building structure, with an elevated exterior drive lane and drop off area above the first floor. Not something you see everyday, or want to! I appreciate any input/expertise to see if I am approaching this correctly.
I have a project that involves an exterior elevated driveway over the first story of a building (HS-20 loading). The driveway consists of a radiant heated concrete deck (7-9" depth) on top of high density rigid insulation (4" min), waterproofing membrane, supported by a structural reinforced concrete deck on 1-1/2" inverted composite decking. The driveway is supported by wide flange structural steel beams spaced 5 ft. on center, parallel with the "traffic" lanes. Girders are spaced every 30 ft. perpendicular to the drive lanes.
I believe I need to consider two loading conditions: 1. (Max tire load) 16 kip point load (10"x20" contact area), and 2. (Lane loading) A 640 lb/ft uniform load plus 18 kip and 26 kip point loads for maximum moment and shear distributed over a 10 ft. length. I do not think the lane loading will control in this case. I found a reference that the effective width "B" of slab used for design can be taken as B = 4 + 0.06*L (ft.) where L is the center to center spacing of supports. In my case, L is 5 ft., so B is equal to 4.3 ft. Seems reasonable, but that is quite a bit wider than the tire contact, so I'm not sure if it is conservative. I also assume you need to follow the AASHTO load factors for DL and LL with impact considered instead of ACI load factors in this case.
This is a bit tricky as its a building structure, with an elevated exterior drive lane and drop off area above the first floor. Not something you see everyday, or want to! I appreciate any input/expertise to see if I am approaching this correctly.